I think I have a plan but I want to make sure this is going to work before I order it.
Here are the detail on the well pump -
2HP
Externally regulated gen requirement 7.5Kw
Internally regulated gen requirement 4
240
13.5 max service amps
Right now it is connected off of a double pole 40A breaker.
I'm hoping this will work as a transfer switch - I'll have an electrician install it but I want to make sure I have the right part on hand when I set up the install.
http://www.reliancecontrols.com/Prod...il.aspx?CSR302
MODEL CSR302 MODEL DESCRIPTION Easy/Tran MAX. GENERATOR RUNNING WATTS 7500 PHASE Single MAX. SINGLE-POLE CIRCUITS 2 MAX. DOUBLE-POLE CIRCUITS 1 MAX. COMBINED LOAD @ 125 VAC 60 MAX. COMBINED LOAD @ 250 VAC 30 POWER INLET, NEMA L14-30 RECCOMMENDED CORD SIZE [gauge] 10 WATTMETERS No SHIPPING WEIGHT [lbs.] 11 DIMENSIONS H x W x D [inches] 8.75 x 7.5 x 6.25 CABINET TYPE, NEMA Outdoor, NEMA 3R