One of the things that was in my Inspection Objection for selling my house was that there are outlets throughout my house that are not grounded. Digging around I noticed some outlets showed they were grounded some did not. After comparing the two, the grounded outlets are grounded to the metal outlet box. Apparently when whoever remodeled, they replaced the metal electrical box with the blue plastic box throughout the common area (living room, hallway). The Romex is 3 wire but they cut the ground wire back. It is still accessible if need be. But when I spliced into that ground cable and wired everything up it still showed an "open ground".
Is there a way to ground these boxes? I know I can replace them all with GFCI outlets but Id rather not spend $100 on outlets.
Thanks again guys!