    I think I have a plan but I want to make sure this is going to work before I order it.

    Here are the detail on the well pump -

    2HP
    Externally regulated gen requirement 7.5Kw
    Internally regulated gen requirement 4
    240
    13.5 max service amps

    Right now it is connected off of a double pole 40A breaker.

    I'm hoping this will work as a transfer switch - I'll have an electrician install it but I want to make sure I have the right part on hand when I set up the install.

    http://www.reliancecontrols.com/Prod...il.aspx?CSR302

    MODEL CSR302
    MODEL DESCRIPTION Easy/Tran
    MAX. GENERATOR RUNNING WATTS 7500
    PHASE Single
    MAX. SINGLE-POLE CIRCUITS 2
    MAX. DOUBLE-POLE CIRCUITS 1
    MAX. COMBINED LOAD @ 125 VAC 60
    MAX. COMBINED LOAD @ 250 VAC 30
    POWER INLET, NEMA L14-30
    RECCOMMENDED CORD SIZE [gauge] 10
    WATTMETERS No
    SHIPPING WEIGHT [lbs.] 11
    DIMENSIONS H x W x D [inches] 8.75 x 7.5 x 6.25
    CABINET TYPE, NEMA Outdoor, NEMA 3R

  2. #12
    Machine Gunner th3w01f's Avatar
    Join Date
    Nov 2010
    Location
    Castle Rock, CO
    Posts
    1,626

    Default

    I've also realized that a 7.5KW generator isn't going to be cheap. I hadn't expected them to be as expensive as they are.

    I guess I should add that I've been looking at Honda generators which is where the sticker shock came from. Who else makes high quality generators that can be depended on?