    Default Basement Electical Question

    Finishing a basement, running #6 conductors to a sub panel off the main in the garage. The entire path will be in wall or ceiling.

    Question, do I need to run conduit for the 3 insulated conductors and the ground? Does not seem like I should but code is not logic...

  2. #2
    Paper Hunter
    Join Date
    Aug 2007
    Location
    Sheridan
    Posts
    132

    Default

    Individual conductors (not in a factory made cable) must be in a continuous conduit run

  3. #3
    If I had a son he would look like....Ben SideShow Bob's Avatar
    Join Date
    Mar 2010
    Location
    SE Aurora
    Posts
    7,121

    Default

    Yes, unless it is an SO type cord rated for use in that type of manner.
    IE, hot tub or range type of 3 conductor cable with ground.
    Three individual conductors and a ground is a big No No without conduit.


    Edit: DWW beat me to it.
    My T.P. wheeling and dealing feedback is here.

    Opinions are like assholes, everybody has one, and it stinks more than mine.


    Yo Homie, That my chainsaw ?



    Pati, improbe et vince

  4. #4
    If I had a son he would look like....Ben SideShow Bob's Avatar
    Join Date
    Mar 2010
    Location
    SE Aurora
    Posts
    7,121

    Default

    You could put your sub panel next to the main and rope your circuits to the basement.
    Remember, code says all remodel work needs to meet current codes, so the new circuits need to be arc fault protected no matter where the sub panel is located.
    My T.P. wheeling and dealing feedback is here.

    Opinions are like assholes, everybody has one, and it stinks more than mine.


    Yo Homie, That my chainsaw ?



    Pati, improbe et vince

  5. #5
    Machine Gunner esaabye's Avatar
    Join Date
    Apr 2009
    Location
    Northern Colorado Springs
    Posts
    1,217

    Default

    Was worried that would be the answer, so it looks like 1 1/4 to hold the 3 #4 and 1 #6 according to the book, correct?

  6. #6
    Paper Hunter
    Join Date
    Aug 2007
    Location
    Sheridan
    Posts
    132

    Default

    What size breaker are you feeding the panel with? In your first post you said #6's that would work out to a 60 amp breaker, 3 #6 & 1 #10 ground will go in a 3/4" 60 is usually plenty for a basement. If you want to do 4's that works out to a 80 amp breaker, 3 #4's & #8 ground will go in a 1" not sure about the availability of the 80 amp breaker. Remember to float the neutral and use bushings, bonding on at least one end

  7. #7
    Machine Gunner esaabye's Avatar
    Join Date
    Apr 2009
    Location
    Northern Colorado Springs
    Posts
    1,217

    Default

    running a 70 amp breaker, so 1 1/4 it is... Running the #4 (miss typed first post) so we have the option for 100 down the road if needed.

  8. #8
    Paper Hunter
    Join Date
    Aug 2007
    Location
    Sheridan
    Posts
    132

    Default

    Quote Originally Posted by SideShow Bob View Post
    Remember, code says all remodel work needs to meet current codes, so the new circuits need to be arc fault protected no matter where the sub panel is located.
    Also remember all arc fault breakers are full size

  9. #9
    If I had a son he would look like....Ben SideShow Bob's Avatar
    Join Date
    Mar 2010
    Location
    SE Aurora
    Posts
    7,121

    Default

    Though the code says 3-#4s & a #8 ground is permissible in a 1" conduit, for the minor extra expense go with the 1 1/4" conduit. Especially in the confines of a residential remodel. The ease of pulling through the larger conduit will outweigh the few extra dollars spent.
    You will thank yourself afterwards.
    My T.P. wheeling and dealing feedback is here.

    Opinions are like assholes, everybody has one, and it stinks more than mine.


    Yo Homie, That my chainsaw ?



    Pati, improbe et vince

  10. #10
    Machine Gunner esaabye's Avatar
    Join Date
    Apr 2009
    Location
    Northern Colorado Springs
    Posts
    1,217

    Default

    OK, were does one find SER cable?

    yes, already have 50ft of the other..