Was worried that would be the answer, so it looks like 1 1/4 to hold the 3 #4 and 1 #6 according to the book, correct?
Was worried that would be the answer, so it looks like 1 1/4 to hold the 3 #4 and 1 #6 according to the book, correct?
What size breaker are you feeding the panel with? In your first post you said #6's that would work out to a 60 amp breaker, 3 #6 & 1 #10 ground will go in a 3/4" 60 is usually plenty for a basement. If you want to do 4's that works out to a 80 amp breaker, 3 #4's & #8 ground will go in a 1" not sure about the availability of the 80 amp breaker. Remember to float the neutral and use bushings, bonding on at least one end
running a 70 amp breaker, so 1 1/4 it is... Running the #4 (miss typed first post) so we have the option for 100 down the road if needed.
Run some SER cable. No conduit needed.
My T.P. wheeling and dealing feedback is here.
Opinions are like assholes, everybody has one, and it stinks more than mine.
Yo Homie, That my chainsaw ?
Pati, improbe et vince
That's a better solution but it sounds like he has wire he wants to use up. #4 is not good for 100 amps. If you're going conduit and you think you might want 100 amps down the road then do run 1 1/4" or make life easier and run ser cable good for the 100 be sure to use deox