    Was worried that would be the answer, so it looks like 1 1/4 to hold the 3 #4 and 1 #6 according to the book, correct?

  2. #2
    Paper Hunter
    Join Date
    Aug 2007
    Location
    Sheridan
    Posts
    132

    Default

    What size breaker are you feeding the panel with? In your first post you said #6's that would work out to a 60 amp breaker, 3 #6 & 1 #10 ground will go in a 3/4" 60 is usually plenty for a basement. If you want to do 4's that works out to a 80 amp breaker, 3 #4's & #8 ground will go in a 1" not sure about the availability of the 80 amp breaker. Remember to float the neutral and use bushings, bonding on at least one end

  3. #3
    Machine Gunner esaabye's Avatar
    Join Date
    Apr 2009
    Location
    Northern Colorado Springs
    Posts
    1,217

    Default

    running a 70 amp breaker, so 1 1/4 it is... Running the #4 (miss typed first post) so we have the option for 100 down the road if needed.

  4. #4
    CO AR-15's very own Gimli Sparky's Avatar
    Join Date
    Oct 2003
    Location
    Lakewood
    Posts
    2,267

    Default

    Run some SER cable. No conduit needed.

  5. #5
    If I had a son he would look like....Ben SideShow Bob's Avatar
    Join Date
    Mar 2010
    Location
    SE Aurora
    Posts
    7,121

    Default

    Quote Originally Posted by Sparky View Post
    Run some SER cable. No conduit needed.
    That is what I meant, not SO. Thanks......
    My T.P. wheeling and dealing feedback is here.

    Opinions are like assholes, everybody has one, and it stinks more than mine.


    Yo Homie, That my chainsaw ?



    Pati, improbe et vince

  6. #6
    Paper Hunter
    Join Date
    Aug 2007
    Location
    Sheridan
    Posts
    132

    Default

    Quote Originally Posted by Sparky View Post
    Run some SER cable. No conduit needed.
    That's a better solution but it sounds like he has wire he wants to use up. #4 is not good for 100 amps. If you're going conduit and you think you might want 100 amps down the road then do run 1 1/4" or make life easier and run ser cable good for the 100 be sure to use deox

    Edit; posting from the phone sucks